yes certainly can. The site is in the middle of a field hence 300mts away. Got overhead power line near but not going to be able to tap into them!!

No but the DNO can! This solution could be much better in the long run as you could expend your glamping bussiness. Extend your existing LV supply is limiting.
 
Definitely worth getting proper design input based on an accurate site survey at this stage as it could save £££.

To expand on James' comments, if your supply is actually 'split-phase' 230/460V, and if both lines can be used with equal design load on each e.g. one pod per line, this configuration saves copper with minimal extra work. A 3-core cable would be needed but only half the conductor size, so the same voltage drop could be achieved with only 3/4 of the amount of copper, compared to single-phase 230V. That's the worst case when completely unbalanced, with 4kW load on one line and nothing on the other. When the load is balanced the drop will be halved even with a cable half the size, so you would save a few % on the electricity bill.

Adding a transformer at the pod end would remove the need for a neutral and allow the use of a 2-core cable one quarter of the size, since all load would be carried at 460V. The saving would have to be offset against the purchase and running cost of the transformer which would need calculating and might not be economic.
 
yes certainly can. The site is in the middle of a field hence 300mts away. Got overhead power line near but not going to be able to tap into them!!

Near to where the pods are going to be?

As others have said you can't tap in to them, but the DNO can and that may be cheaper than a correctly sized cable and have the advantage of not having any volt drop or any issues with earthing due to the circuit length.
[automerge]1595349423[/automerge]
Is it worth considering running both phases down a cable to a transformer near the pods.
This would need to be properly designed but volt drop would be roughly half and you could use the right transformer taps to ensure correct voltage at point of use.

I looked at this option a few months ago for a 3 phase supply over a similar distance, the transformer option was prohibitively expensive when the ongoing maintainence cost, and downtime should the transformer fail, we're factored in.
 
I agree that the transformer option might not be useful here, although with a split-phase supply available, the advantage is slightly greater than with 3-phase. Sending the split-phase down the cable is likely to be worthwhile though, as the plant cost and losses are both lower than with single-phase.
 
An idle moment with on-line tools is saying 50mm and around £3k of cable (BEFORE the cost of installing is factored in) and over 1/2 tonne of it to be wrangled. So you really want to make sure it is the right choice!
 
An idle moment with on-line tools is saying 50mm and around £3k of cable (BEFORE the cost of installing is factored in) and over 1/2 tonne of it to be wrangled. So you really want to make sure it is the right choice!

What parameters were you putting in to the online tool?
 
230V single phase, 8kW, 5% drop, 330m, direct in ground method.
[automerge]1595403097[/automerge]
Assuming one sub-main run to both pods and then some splitting arrangement at the end for the pods to share that as needed.
[automerge]1595403439[/automerge]
Of course you don't gamble £3k of cable plus significant installation expenses on an on-line tool's results, you get someone to go through the design properly!
 
Last edited:
230V single phase, 8kW, 5% drop, 330m, direct in ground method.

Ah OK, that explains the difference from my estimate of 95mm, I was basing it on a 3% (ish) drop and a 40A supply.

I think 40A may still be a bit low without further information on the klargester sewage plant. Plus I think it is fair to assume that there will be water heating of some sort not mentioned by the OP, the presence of the klargester suggests that there will be some sanitary facilities nearby, probably a small building with W/C and washing facilities.
 
Ah OK, that explains the difference from my estimate of 95mm, I was basing it on a 3% (ish) drop and a 40A supply.
I would usually assume 5% is OK for such a sub-main even though there are lights on it as most likely no one load is going to change the supply be much more than 1%.

I think 40A may still be a bit low without further information on the klargester sewage plant. Plus I think it is fair to assume that there will be water heating of some sort not mentioned by the OP, the presence of the klargester suggests that there will be some sanitary facilities nearby, probably a small building with W/C and washing facilities.
Very true, also 4kW max load seems small if any heating & cooking together is possible. But I have never "glamped" to know what sort of joys it provides in this way.
 
Ah OK, that explains the difference from my estimate of 95mm, I was basing it on a 3% (ish) drop and a 40A supply.

I think 40A may still be a bit low without further information on the klargester sewage plant. Plus I think it is fair to assume that there will be water heating of some sort not mentioned by the OP, the presence of the klargester suggests that there will be some sanitary facilities nearby, probably a small building with W/C and washing facilities.
No heating and hot water will be via LPG boiler.
They state the klargester at no more than 300w
 
How far apart are the two glamping pods?

As already covered, you need to be very sure of the total load, and the distances involved, and any plans for the foreseeable future (e.g. any more pods, or any extra facilities like heating), as the installation costs will not be cheap and will cost you a lot more if it is over-specified (or worse and under-specified so has to be replaced).

There are always many way to do something and good engineering is the art of compromise - to meet the goals of safety and functionality at the best price.

With such a cable length you are looking at a lot of metal, and that is expensive, but some of the suggestions still may not be cost-effective in this case. For example, the idea of using 2-core cable from your 480V split supply could save a lot of cable costs, but unless it is well over £1k savings probably won't pay for the transformer. Also transformers have some losses, so trading off the running cost difference may not be so obvious.

You can get aluminium cable but that is rare to see in the UK outside of the electricity supply network and big factories. Aluminium is about 50% higher resistance than copper but much cheaper, so going up a size can still be cheaper in overall cable cost for similar ratings. But it is a pain to work with as usually solid inflexible cores and you need to take special precautions when terminating to avoid galvanic corrosion between aluminium and copper/brass/etc in most equipment. In your case again it looks to be below the point when it would be worth looking at Al cable options (most sparkys would steer clear of that option).

Same for other clever solutions like local power storage to allow a kettle or similar to run at high power for 5-10 minutes with the overall cable load being less for a longer period. While it looks like a neat idea, it probably won't be cost effective and adds a significant reliability question due to the complexity.

So it looks like your best option is going to be just a lot of copper cable. A quick look at the 50mm case would suggest that 2-core cable using the armour for earth is probably just usable with a 40A fuse protecting the feed, but that would very much depend on your supply characteristics. If your supply Ze does not permit that option, it may be most cost-effective to put a time-delay 300mA RCD (or similar) up front to clear cable faults while maintaining selectivity with the galamping circuits on RCBOs, etc., rather than go for 3-core cable to lower R2 as that extra copper core will add something like £4/m to the raw cable cost.
 
Last edited:
Hi - to throw in another idea - though perhaps not cheaper - solar panels, storage battery and invertor with a small gas powered generator to keep it topped up as may be necessary from time to time.
@marconi
 
See my #20 in

need to solve voltage drop over long run - https://www.electriciansforums.net/threads/need-to-solve-voltage-drop-over-long-run.187671/#post-1638711

Top 'line diagram' is the conventional long thick cable solution.

Bottom line diagram is local short term 'heavy lifting' provided by battery and inverter. Battery charged by solar pv or thinner long cable or both. Voltage stability and load capacity for glamping provided by inverter.

Or maybe no long cable run at all and have two battery banks - one at the glamping site and the other being charged at the farm which are swapped over say daily. Especial care would have to be taken with the way the batteries are transported back and forth and connected because of the dangers associated with very high energy density batteries - this would not be a preferred practical way ahead so keep it at the back of your mind for now unless the cable run is very expensive. Nota bene - not a task for glampers to do.
 
Last edited:
Whilst 'Glamping' is a relatively new style of recreational accommodation, caravan sites etc are not. Why not just follow the old style format? As said, you'll probably end up with more.

PS, have you watched Four in a Bed much OP, a lot say 'No, to would you stay here again!'.
 
By my rough reckoning parallel cables will be the most cost effective solution, as long as the design is done right.
 