D diditrain ~ Arms Jun 11, 2009 #1 Hi all, if a supply to an outhouse is ran through an overhead length of steel pipe, is it necessary to bond the metal pipe? My thinking is that the pipe is an exposed conductive part and therefore should be bonded Could anyone clarify. Many thank`s
Hi all, if a supply to an outhouse is ran through an overhead length of steel pipe, is it necessary to bond the metal pipe? My thinking is that the pipe is an exposed conductive part and therefore should be bonded Could anyone clarify. Many thank`s
G grandad Jun 14, 2009 #3 Jason.S said: I would say yes, unless the cable inside is SWA Click to expand... definately yes....even if the supply is SWA it is a conductive containment .treat it as trunking /tray/ladder rack/conduit and bond it as you are supposed to
Jason.S said: I would say yes, unless the cable inside is SWA Click to expand... definately yes....even if the supply is SWA it is a conductive containment .treat it as trunking /tray/ladder rack/conduit and bond it as you are supposed to