NO it's not to do with checking old cables, though it can be used to do so. Sheath testing is normally primarily made to New cables before final gland termination to enclosures.
Testing is performed between the SWA, to either a spike or more likely, proven earthed metalwork etc. Obviously the SWA must not be in contact with any earthed metalwork during the the testing period.
You may well have pulled in many cables in the past without undertaking sheath testing, So you'll never know if any of those cables SWA's are now corroding away or not. Any large project with project supervision, that requires work signing off before payments are released will most certainly be conducting such tests on direct buried cables.
One thing is for sure, roughly handled cables, bad pulling techniques, lack of attention to back filling procedures, and the chances are you will get a failed sheath test guaranteed!! Which is going to bad news where installations are relying on the SWA as it's primary source of earthing/CPC.
ah right so its to check for a break in the sheath and to test if the armourings are in contact with the earth meaning if it is the armours are going to rust away. now i know why id never heard of the test before all the swas we pull in are 99% of the time on ladder racking or on trays