Many thanks for your reply Richard Burns which makes lots of sense, behind the use of a banjo.
Although i wish the locking nuts provided were just a fraction thicker to get a good purchase on when tightening but thats obviously cut backs, i quite often use piranha and flying earth lead, my companion debated that if earth continuity was present with as he said measured to 0.00 ohms on meter is that not sufficient continuity, i gracefully conceded the debate.
 
So Pete999 - a banjo - fixed to the CU with a nut and bolt and a fly lead?
Could do it that way I prefer a Piranha nut a far better and neater appr
It has the banjo fitted so it must be fine!!!
What on earth did they manage to do to that gland to rip off the end of the clamp nut?

They cut the Armour out of the equation Richard, because they didn't know how to do it properly, you can see from the pics that the Armour was/is /wouldn't reach thecorrect position to form a proper termination.
 
Last edited:
my companion debated that if earth continuity was present with as he said measured to 0.00 ohms on meter is that not sufficient continuity, i gracefully conceded the debate.

I don't quite understand this bit. What did your companion actually measure between to get this reading? How accurate is his meter?
 
It is the reliability of the connection that is the issue, with a very short distance from gland to metal it is easy to get a 0.00Ω measurement but the contact area could be only 0.5mm² and this may not withstand an earth fault current, melt and and so leave the armour disconnected at the very time it is needing to be earthed.
 
I use these when terminating into a plastic box. Great way to maintain earth continuity

20171107_094750.jpg
 
Interesting thread .................. especially for those who insist on using 2 core SWA and use the CPC to the outer protection .....................

I prefer to use 3 core ..........
When using swa for the ‘tails’ I use 2 core 25mm swa and a 16mm earthing conductor in parallel
 
When using swa for the ‘tails’ I use 2 core 25mm swa and a 16mm earthing conductor in parallel

So what's the price comparison between the above and 3 core SWA?
I haven't got the charts on me at the mo but isn't the armour on 25mm sufficient for the earth?
 
The armour would not be 16mm equivalent copper as I’m talking about the main earthing conductor
Also if I used 3 core then a 25mm earth conductor is way overkill
 
The armour would not be 16mm equivalent copper as I’m talking about the main earthing conductor

That's what I was going on about. I will have to look that up as I thought it would be.
 
The armour can be used as a cpc but it won’t be 16mm CSA copper equivalent which is what the DNO require on a new supply
 