What test equipment do you have?
I think that would depend which end of the SWA is measured to earth, presumably, at the MET? If measured at the 'other end you would be measuring the resistance of the armour.
What test equipment do you have?
How's that then?? your testing between totally isolated armouring and earth!! Any reading will indicate that the PVC has been damaged and allowing moisture into the cable. The fact that continuity has been lost on one of the core's indicates severe damage. The cable needs replacing or if at all possible, repair jointing at the damage point...
Surely if the cable was damaged the a protective device would have been tripped - I am assuming that the cable was live at one stage.
Need more information!!
Yep this getting silly and yet again little or no information a lot of guys speculting trying to help out and we will never get to hear the end of it or we might get I sorted it comment
Sorry about the delay in responding to your further queries - was called away.
The cores provided a ring circuit with red (live) and black (neutral) with the return being yellow (live) and blue (neutral) with the armour providing CPC. We moved in a couple of months ago and have not used the garden room - I plugged in a fan and it tripped.
On testing the cores and the armour there is continuity in all but the yellow core. I have tested the IR and that is good although not clear - reading 140 mohms - used a Megger MFT.
My thoughts are to convert to a radial and reduce the protective device from a rating of 32A to 16A.