can anyone tell me what the current carrying capacity is for a 6mm SY 3 core cable , or where i can find a table or do i just go by the 70* thermoplastc table in the regs book
 
From memory it is about 43-44A I think but I could be wrong. I don't believe it is included in the BGB as I had to get that info from manufacturer.
 
I seem to remember there was a discussion a while back about whether SY is OK for carrying mains or not? Think Malc had something to say on the matter???
 