There are two aspects to consider :Hi, I have 2 consumer units, one downstream of the other, connected via 10mm2 3-core SY cable. 50A MCB. No RCD protection. Am I correct in thinking that SY isn’t suitable and should be replaced?
Thanks Simon.There are two aspects to consider :
1) Is it safe ?
Provided it's properly installed (especially terminations using correct crimps or ferrules), then it should be safe.
2) Is it compliant ?
Comes up from time to time, SY along with its siblings CY and YY isn't made to a standard recognised by BS7671. So it's use is non-compliant.
My personal view would be that unless there's something wrong with the way it's installed, then leave it as it is.
Not the line ?... but ferrule the neutral and cpc..
Terminated at an MCB would be far better without a ferrule in my opinion.Not the line ?
Ah, I guess you are assuming that's in a box clamp. I.m.o. that still needs a ferrule for fine strand cable.
I think we'll need to respectfully disagree on that one.Terminated at an MCB would be far better without a ferrule in my opinion.