SY distribution cable

mattreay

Supporter
Hi, I have 2 consumer units, one downstream of the other, connected via 10mm2 3-core SY cable. 50A MCB. No RCD protection. Am I correct in thinking that SY isn’t suitable and should be replaced?
 
Hi, I have 2 consumer units, one downstream of the other, connected via 10mm2 3-core SY cable. 50A MCB. No RCD protection. Am I correct in thinking that SY isn’t suitable and should be replaced?
There are two aspects to consider :

1) Is it safe ?
Provided it's properly installed (especially terminations using correct crimps or ferrules), then it should be safe.

2) Is it compliant ?
Comes up from time to time, SY along with its siblings CY and YY isn't made to a standard recognised by BS7671. So it's use is non-compliant.

My personal view would be that unless there's something wrong with the way it's installed, then leave it as it is.
 
There are two aspects to consider :

1) Is it safe ?
Provided it's properly installed (especially terminations using correct crimps or ferrules), then it should be safe.

2) Is it compliant ?
Comes up from time to time, SY along with its siblings CY and YY isn't made to a standard recognised by BS7671. So it's use is non-compliant.

My personal view would be that unless there's something wrong with the way it's installed, then leave it as it is.
Thanks Simon.
It hasn’t been crimped, but the upstream board is being replaced which will be an opportunity to rectify that. On the EIC for the upstream board replacement would you mark it as a departure?
 
Strictly speaking it an existing part of the installation so not really relevant to your works but ferrule the neutral and cpc. If it is easy to replace then it is up to you.
 
Not the line ?

Ah, I guess you are assuming that's in a box clamp. I.m.o. that still needs a ferrule for fine strand cable.
Terminated at an MCB would be far better without a ferrule in my opinion.
 