t&e and singles

H

Hawk

Is there anything wrong with having t&e mixed with singles on a ring circuit? For example a kitchen ring with conduit linking everything. The 2 legs coming from the garage would be t&e as they will be clipped to joists. But as everything in the kitchen will be conduit it would be easier to pull singles than trying to pull 2 t&e cables down a conduit. Can't see anything in the regs advising against this.
 
how are you connecting the T/E to the singles? arew you using conduit as cpc or a separate conductor. more info needed to give definitive reply.
 
So single brown, blue and earth. The t&e will connect to the singles in the first and last socket on the ring.
 
if its plastic conduit I am assuming there is a separated cpc single being used- so along as you have ring continuity on r1 rn r2- I can't see it being an issue?
 
can't see any problems as long as everything is done to regs. and cont. tests are ok.
 
i've got some 7/029 singles he can have. it's red/black, so should blend in nicely. :computer:
 
i've got some 7/029 singles he can have. it's red/black, so should blend in nicely. :computer:

As an apprentice when the colour change happened I had the fun of clearing all of the old colour cable out of the stores. Along with the usual array of SWA offcuts and half drums of singles there were some imperial singles, a complete drum of lead twin, TRS and VIR hiding away at the back of the stores.
That company never threw anything away!
 
Straight to the scrap man Dave? Lol. And to answer your question 2.5mm singles + t&e

No comment ;)

Not a 1.5 single for the cpc then? Won't that make your calculations a bit more tricky and your test results a bit harder to interpret?
 
I've done that several times ran most of the ring in t&e and then dropped a few links in , in conduit and singles. Done it a few times when wiring sockets in a conservatory and having to span a doorway. Nothing wrong with it aslong as all singles are enclosed in containment
 
I'm not sure how to word this...
Cables in trunking over head (maybe not the read word to use but about that high) need to be tied down, in such a way that when if the trunking melts in a fire, that the cables don't hang around and catch people trying to leave. Also they maybe still live.

https://www.google.co.uk/url?sa=t&source=web&rct=j&url=http://www.ifpo.org.uk/downloads/assemblage3presentation2014.pdf&ved=0CF4QFjAEahUKE*wjk-aDUmcvHAhUMm9sKHZEuCBI&usg=AFQjCNF-E8-iH_Y_ZVDD1szJrYX2ldH6TQ&sig2=V4nA-xwrTnb9y9PVvCzdsw
 
Last edited by a moderator:
I'm not sure how to word this...
Cables in trunking over head (maybe not the read word to use but about that high) need to be tied down, in such a way that when if the trunking melts in a fire, that the cables don't hang around and catch people trying to leave. Also they maybe still live.