Monkey1984

Is there a reference method for just clipping T&E to a wall - Not enclosed in conduit / trunking but just clipped. Or is this a frowned upon method and shouldn't be done.

Just having a discussion and this question come up.

Answers on a postcard job :)
 
Yes, see table 4A2 (page 265) in BS7671 for T&E...or Page 262 number 20 for multicore cable.

No problem doing clipped direct, and in some instances it is a good method as the cables are visible and therefore reduces the risks of mechanical damage, and also mitigates the need for an RCD for circuits not supplying sockets.

Yooj
 
Yes, see table 4A2 (page 265) in BS7671 for T&E...or Page 262 number 20 for multicore cable.

No problem doing clipped direct, and in some instances it is a good method as the cables are visible and therefore reduces the risks of mechanical damage, and also mitigates the need for an RCD for circuits not supplying sockets.

Yooj

Yeah i have the regs in front of me now - I can see what you mean on 262.

The only reason it came up is because he put a new feed in for a boiler - (Customer had no heat or water since march!) the sfcu was on the work surface so he put some trunking in from the sfcu to below the work surface (To prevent damage from things being thrown on the worktop) and then clipped it directly to the wall underneath.

He says the same thing as you do its there and clipped so its easily seen and can't be hit with anything - However he is now wondering if he should go back and put that final leg into trunking instead. Hence the question about reference methods in the regs.
 