The sub db will only supplying a 1.5kw inverterWhat is the prospective load for this board?
I was concerned with it being a 100amp main fuse that 16mm tails are okYou can go smaller than 16.0mm² if that is the case.
Even though the load will not be more than 1.5kw on that db. It’s more the 16mm tails can take 87amps but they’ll be protected by the 100amp cut outOne circuit loaded at 1.5KW how is it going to achieve 100A on the tails?