Reaction score
645
Thought I share this with you,arrived on site to start a 1st fix on school classrooms,saw temp electrics to cabins,for site agent & mess rm.First impression rough,sy cable used ,we all know hassle with that,looked at DB ,hanging from the DB a 10 mm earth cable,not connected.Asked site agent who did the temps,it wasn't our company,so carried on with my other works.
later on,site agent wants some temp external power installed,& wants us to do it.
So installed power,& tested,Supply cable loop impedance,at DB did not comply,& would not disconnect on fault conditions.
Earth for temps,Swa sheath used,does not comply.
Earth cable from DB not connected to earth rod.
So,told site agent,he called guys who installed electrics,they phone me,the complete nonsense & crap from the electrician & his boss,I really could not believe,giving me its ok, the mcb will be fine you are allowed 2 ohms on a 40 amp c type.
Anyway the 2 electricians come over,spoke to them about my opinions,that went down well,No,they put a rcd upfront,sat in the van,still no electrode fitted,frustrating, does anyone care.
By the way it's a pme system.
 
Will they even bother looking,the company who employed them think they are wonderful,haven't yet seen certificate,still no proper earthing system,still Pme to metal cabins & no real main bonding.
 

Reply to Temp supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi, I’m an industrial electrician, so when it comes to DB regs and such my experience on them is a little limited. I need 2 x 16A 3 phase supply...
Replies
1
Views
679
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Replies
2
Views
649
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock