Philip657

Hello all wonder if someone can give me some advice.
i just rebuilt my house and got the builders sparky to do the job as it was to big for me.
but i want to question his testing. He has given me a test cert that is the one from NAPIT to say its been registered but he has not given me the on that has all the results on. does he have to give me the one that shows all the results ?

he has signed this off but we still have 3 outside light fittings not fitted and the cable is just poking out the wall. i know the "lamp" has to be isolated but can this installation be signed of without the fittings being fitted ?

is this just bad practice but within regs ? or is this acceptable

Thanks Philip
 
You are within your "rights" to ask for the full EIC which should be 3, 4 or 5 pages, depending on which type of certificate/software he is using.

Regarding the cables poking out of walls - has this been agreed? If not I wouldn't pay him til its done.

Just re-read your post - he's shown you the certificate to show its been registered - sounds like the first step of the LABC notification. In which case ask him for the EIC in full.
 
Last edited by a moderator:
If he has given you a NAPIT certificate,
does it have his NAPIT membership number?
If it has then he is a member and should be Part P registered
If he is not the as it has been mentioned above he maybe going though LABC
either way if the lights have not been fitted, then the live testing has not been carried out.
Part of the NAPIT membership is a customer complaints procedure.
If you are not happy with the way he has handled your complaint then go to NAPIT
NAPIT will warranty a members work for 5 years.
so first of all is this guy a NAPIT member?
He should have a photo ID card that gives his membership number with the expiry date.
 
Thanks guys

i have managed to get him round after speaking to NAPIT. and i am gobsmacked. this is the first time i have been home and watched him work. we are a small domestic home with only me home. he just cuts the wire with power on and lets it just short out to turn the power off. and he never double checks to make sure its safe to work on. hes now installed 2 outside lights for me but hes never got his meter out of his van.

then he tryed giving me a test cert :S sorry i am not a tester my self. but i know a little bit about it. am i right in saying that he should have done insulation Resistance and Zs readings on the new lights ?


Thanks guys
 
If that's his method of safe isolation then imho the man is an idiot. Your circuit should be fully tested not just IR and Zs and you should get the full EIC which as previously stated would be a multipage document, one of which will be a schedule of test results
 
As you noted in your original OP the outside lighting circuit was already there, so i'm assuming he was just fitting the lights today.

Really he should have tested the circuit before he fitted the lights, as it is much easier and so not surprised that he never issued a certificate for today's work, but did you mention certification to him
 
tell me about it. i am still stuck on the sofa in shock.
Malcolm yes the wiring was in place but was only taped over so one wire from the connections then next to it there was another wire that was dead next to it ready for the next light. i can believe he may of tested the first light when he wired it. but i dont believe he would have tested the second light wiring.


http://www.electriciansforums.net/members/malcolmsanford.html
 
if you have a decent sum of monies held back, i would be inclined to get an independent, qualified and registered sparks to check his work. whatever this costs can be deducted from what you owe the original sparks. any problems found, though, you would have to address separately, depending on what your 2nd sparks found.
 
For non minor works, as described, you must receive an electrical installation certificate, a schedule of test results and a schedule of inspections. The certification should say on it that the EIC is not valid without the SoTR and SoI.
It is possible (but sounds unlikely in this case) that he has done all the necessary tests and inspections before fitting the lights (except for functional testing).
I do remember being advised by a builder when I was trying to trace a circuit "just join the wires together and whichever MCB trips is the right circuit" I just looked at him in disbelief; obviously this is standard practice for dead builders!!
Do not pay him until you have the correct paperwork, or follow Tel's suggestion, but do give him a chance to explain first.
 
thanks guys i think for my own peace of mind i may get someone round. as watching this guy has scared me :S. i am not a "true" sparky but i know whats safe and safe practices and he dident follow any of them.

does anyone know any good sparkys in the west London area? how how much would i expect to pay for a 11 circuit PIR and to test/ check everything this guy has done

Thanks for all the help

phil
 
You are within your "rights" to ask for the full EIC which should be 3, 4 or 5 pages, depending on which type of certificate/software he is using.

Regarding the cables poking out of walls - has this been agreed? If not I wouldn't pay him til its done.

Just re-read your post - he's shown you the certificate to show its been registered - sounds like the first step of the LABC notification. In which case ask him for the EIC in full.
thing is here n all is the possibility for those cables to become energised by switching....and if the ends have been left bare n all so the possibility of shock exists....if so its a 1 and this "sparky" needs reporting..........
 