Darkwood
Very poor advice ....calculating the correct set-up is the correct method, its within the BS7671 to ensure you design the circuit to avoid small overloads for a long duration 433.1.1-- suggesting downgrading the mcb and see if it keeps tripping is up there with some of the worst advice for a number of reasons .... as a professional or trainee i would suggest you rethink what divides a cowboy sparky from a competent professional.Downgrade the breaker to a 32 amp and if it keeps tripping it needs rewired