G

glasgospark

job today , adding extra lighting and switches for area of house with no lights .
circuit is all metal conduit
twin and earth cable tied to conduit various places with joints made ends twisted together
also spaghetti junction just an eyesore
IMAG0687.jpgIMAG0689.jpg
i refused to add anything to this circuit based on visual inspection and connections/joints i seen
what use guys think
 
it is a attic m8 yeah single core cables in and out of conduit exposed running under n over insulation/joists steel beams etc
 
did you just go to price the job or what? I'd have issue a few c2's minimum by the sounds of it!
 
did you just go to price the job or what? I'd have issue a few c2's minimum by the sounds of it!

it was on a list of things to do , that being the only thing to do requiring attic access and on that circuit ,
other things included extra sockets aerials etc tv on wall...
done everything else on list , obv they didnt want lights rewired there and then ,i advised a more thorough check and explained my thoughts were visual only (not scaremongering) they also recently had a new ensuite installed , including 6downlights , lights were basic cheap and nasty not fire rated or bathroom rated ,covered with insulation advised upgrade in that area and for time being removed insulation from light areas
 
what did they say when you advised an upgrade on work that was recently done?! are you gonna go back and do a more thorough inspection?
 
what did they say when you advised an upgrade on work that was recently done?! are you gonna go back and do a more thorough inspection?

guy wasnt happy said he would call bathroom company regarding that side of it thanked me for taking the time to check all,
regarding the more thorough inspection i gave all advice i could said if u want me back i can spend 1-2 hours checking everything up there and replace/upgrade what i can as i go ,
balls in there court
 
will do , will be same old situ will get spark from gumtree willing to do it lol
 
Are those offcuts or parts of the circuit(s)?

Did the spark(s) / fitters issue certs?

Scrub 2nd question, think I know the answer to that one!!
 