Hi all,

looking for some help, cant get my head round a timer switch I need to install.
it is a TIMEGUARD FST17A.
When you power it up all seems to be fine, its when you switch it off by using the double pole switch on the front of the unit. I seem to be getting some strange readings.

Switch on:
L-N 240v
L-E 240v
N-E 0v

Switch off:
L-N 0v
L-E 0v
N-E 240v ??????

Called help line and guy said it was a capacitive voltage and its normal.

When i set it up to switch on and off some sockets at a test station (solder dip, Extract Fan, Light) and put in socket and see tester it goes mental Phase - Nuetral Reverse

Any help to understand this would be great
 
Try using an analogue tester and see if the test result is the same, if it is then it's not a capacitively coupled voltage. It's a double pole switch on that timer so if the neutral voltage rises it's being back-fed somewhere from the load side.
 
Thanks Marvo for the reply.
I dont have a Analogue Tester, i have set it up in a test are (plug to timer input, socket to output no load) still get the same readings. I did wire a light across E - N when switched off, didnt light voltage droped but came back up when light disconected.
G
 
Timeguard has an issue with these. Call their technical line and they may just put a replacement in the post to you!
 
Thanks again guys,
I have taken one of the other FST17A timer down from a different building and tested that one, that works the way I would expect it.
Seem that I have two faulty units, need to have a stern word with timeguard tech line as I was told that it was normal.
Thanks Marvo, Murdoch response time is excellent.