let me get this straight........
Nic say if you find tns earth connection by means of compression clamp then you cant rely on the integrity of that connection and should convert to TT.
ok , understand that clearly.
then Nic say code it a 2 ??
well if you've then provided your own earth then surely no code for the tns clamp as the dno earth is no longer relied upon ??
not thought through well was it lol.
I'm really tired and I am finding it difficult trying to understand why the nic are telling sparks to meddle with dno equipment, what's next being told its ok to cut the seals and remove the fuse ( at least I've heard of these mystical seals), next they will be saying just connect the main earth to the neutral in the head and turn it into a tn-c-s
I'm really tired and I am finding it difficult trying to understand why the nic are telling sparks to meddle with dno equipment, what's next being told its ok to cut the seals and remove the fuse ( at least I've heard of these mystical seals), next they will be saying just connect the main earth to the neutral in the head and turn it into a tn-c-s

Why on earth is anyone surprised that the NIC are dictating what should be done with DNO equipment? They write their own regs and are masters of the electrical universe, DNOs are mere amateurs by comparison.
Just follow each and all NIC directive without question. They know what they're doing so it'll all be fine.
BTW, are we allowed to swear on here yet? I think it'd be a really good addition to the boards feel and save loads of time. I could reply to each thread mentioning the NIC with five key strokes and two mouse clicks.
Un bloody believable!
let me get this straight........
Nic say if you find tns earth connection by means of compression clamp then you cant rely on the integrity of that connection and should convert to TT.
ok , understand that clearly.
then Nic say code it a 2 ??
well if you've then provided your own earth then surely no code for the tns clamp as the dno earth is no longer relied upon ??
not thought through well was it lol.
done it myself a few times. what is better , a TT with Ze of 150 ohms, or a carefully fitted BS951 to the cable sheath with a Ze of 0.3? i know which i prefer. although a proper spring clamp would be ideal, how many of us carry them on the van?
Just got me thinking, i will be honest i always install an earth clamp to make it a million times safer if there is no main earth
Apparently we're not all singing from the same hymn sheet, as Wirepuller says above a 951 clamp on a lead sheath is not considered to be a sound means of earthing.Why? Thats the problem with this place, every tom and dick starts i asked for an opinion
not the rights or wrongs, we are all singing from the same sheet here no?
Apparently we're not all singing from the same hymn sheet, as Wirepuller says above a 951 clamp on a lead sheath is not considered to be a sound means of earthing.
Suppose you bowl up to a place with a questionable earth reading, you whack a 951 on the sheath and over time it works loose. What happens to that reading you worked so hard to obtain? Or if you'd done this and something were to go horribly wrong, who's --- is in the sling then?
There's a reason why earth rods are easily obtainable mate, plus if it's a DNO earth facility you can get them to come out and rectify it