Hi all

Went to look at a consumer unit change today.
Supply is tncs
all bonding is correct.

I noticed that where the supply is there is no main earthing terminal.
The consumer unit has been used for all bonding and circuit cpcs.

Just wondered weather i should install new met at point of supply and run the cables here or leave at the consumer unit. It will be a bit tricky to do this though.

Just wanted to hear your opinions.

Cheers
 
Thanks guys.
As its a 5 bed house the water and gas points are oposite sides of the house and then the main supply is at the middle.

I think the installers just wanted to make life easier for themselves by running through ceiling voids into the cu.

Ill have to check when i go out next if its viable to run the bonding back to main supply and add a m.e.t
id prefer to do this but depends whats in the way!

Thanks for the replies guys
 
As malcolmsanford says, nothing wrong with the existing situation. There's no regulation that says how close the MET has to be to the supply head, so inside the CU is just fine. Why ask the customer to pay for re-arranging the bonding if it's not needed?
 
I note there's no mention of a main earth in this CU earth bar, have you confirmed it's presence by a properly carried out Ze test?
 
Do whatever you feel most comfortable with, I usually stick an MET next to the CU as I forget to put the bonding wires into the CU first and have to mess up all of my beautifully neat work!
 
Hi all

Went to look at a consumer unit change today.
Supply is tncs
all bonding is correct.

I noticed that where the supply is there is no main earthing terminal.
The consumer unit has been used for all bonding and circuit cpcs.

Just wondered weather i should install new met at point of supply and run the cables here or leave at the consumer unit. It will be a bit tricky to do this though.

Just wanted to hear your opinions.

Cheers
well for a start the less joints you have in a cable...the better as i see it....so you decide....take the main earthing into the C/Us earth bar....or take it to an MET...and from there into the C/Us earth bar?.....your call fella....
 

Reply to Tncs m.e.t in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
554
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock