Two different earthing systems either end of building & yes they can be touched @ the same timeMixed, how? More info needed.
i.e. is it earth rods connected to TNCS, or two entirely separate earthing systems that could be touched at the same time?
I wouldn't be happy.Two different earthing systems either end of building & yes they can be touched @the time
Nor am I …. Would you actually link the 2 Earthing systems togetherI wouldn't be happy.
Thinking the 2 buildings were separate @ some time, then linked with building works making into 1 buildingIt is very wrong and should never have been left like that.
Do you have any idea why there is a TT system installed? Is there a part of the installation which is unsuitable for connection to a TNCS earth?
You can't just connect the two earthing systems together as you could be introducing a potential danger by having a TNCS earth present in a location it shouldn't be.
Thinking the 2 buildings were separate @ some time, then linked with building works making into 1 building
Agree on the danger if being linked with Earthing
THE other option would involve the REC to convert to Tncs…or leave it like it’s been & reported over decades
Ok maybe disconnection of the TT supplyDNO's will not normally provide 2 TNCS earth connections to the same building as that can cause all sorts of problems with diverted neutral currents through bonded metalwork.