TNCS & TT system’s mixed in same building

Discuss TNCS & TT system’s mixed in same building in the UK Electrical Forum area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
650
What’s your thoughts on this both systems are accessible & contact could be made between metallic service‘s, been in service-for ages & only spotted on an EICR
 
I wouldn't be happy.
Nor am I …. Would you actually link the 2 Earthing systems together
Knowing the Zs would be lowered on the TT System
Maybe no difference to having TT & TNCS in close proximity of each other or accidentally linked
The other option would be to disconnect the REC TT supply & reinstate with sub main from the TNCS … no idea the work’s involvement in that
 
It is very wrong and should never have been left like that.

Do you have any idea why there is a TT system installed? Is there a part of the installation which is unsuitable for connection to a TNCS earth?

You can't just connect the two earthing systems together as you could be introducing a potential danger by having a TNCS earth present in a location it shouldn't be.
 
It is very wrong and should never have been left like that.

Do you have any idea why there is a TT system installed? Is there a part of the installation which is unsuitable for connection to a TNCS earth?

You can't just connect the two earthing systems together as you could be introducing a potential danger by having a TNCS earth present in a location it shouldn't be.
Thinking the 2 buildings were separate @ some time, then linked with building works making into 1 building
Agree on the danger if being linked with Earthing
THE other option would involve the REC to convert to Tncs…or leave it like it’s been & reported over decades
 
Thinking the 2 buildings were separate @ some time, then linked with building works making into 1 building
Agree on the danger if being linked with Earthing
THE other option would involve the REC to convert to Tncs…or leave it like it’s been & reported over decades

DNO's will not normally provide 2 TNCS earth connections to the same building as that can cause all sorts of problems with diverted neutral currents through bonded metalwork.
 

Reply to TNCS & TT system’s mixed in same building in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock