Hi all, came to a job the other day, was TNS earthing system also with a rod (TT) has anyone seen this before, test readings Ze and Zs all within TNS limits, maybe the TT was just a back up? If you lose your neutral you’ve lost your earth TNS so can’t really see why there was a rod. If anyone has seen this set up before?
Thanks
 
On a TNS you still have an earth even with loss of the neutral. Some countries do however use an additional rod on a TNCS for that reason.
 
Possibly a TT that’s been changed to TNS. Nothing wrong with leaving the electrode connected.

I work on a lot of street furniture and TN systems with with earth electrodes are a DNO requirement so it’s more common than you think.
 
I came across such an install a few years ago. The previous owner had long gone, so nobody to question. With the rod disconnect I had a suitable test result for the Ze.

I was concerned though, that perhaps the earthing facility had proved unstable previously. So I contacted the DNO, who sent out an engineer. He said there was no history in the area for earthing problems, conducted his own tests, and I enquired about changing to PME system.

We then went into an unusual discussion, as (he said) the application would take some time, and that the supply at some point between this particular supply and elsewhere, had probably been repaired and changed to PME anyway, so why not do it yourself!

Anyway, after asking advice from my Scheme, I removed the connection to the earth rod, and left it as TNS, with a note & pics on the EIC.
 

Reply to TNS and TT combined in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
504
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock