just done some testing in a local resturant my question is do i need to earth metal prep tables all sockets are rcbo protected so in my view no need but another spark has previously flagged this up your thoughts please
just done some testing in a local resturant my question is do i need to earth metal prep tables all sockets are rcbo protected so in my view no need but another spark has previously flagged this up your thoughts please
:rofl:
arty::rockon:set your mft to IR test, 500V. test from the suspect metalwork to the MET
Taking care, if you think it might be an extraneous conductive part, that you don't end up testing the insulation resistance of someone who happens to be holding a different bit of it somewhere else in the building!