just done some testing in a local resturant my question is do i need to earth metal prep tables all sockets are rcbo protected so in my view no need but another spark has previously flagged this up your thoughts please
 
just done some testing in a local resturant my question is do i need to earth metal prep tables all sockets are rcbo protected so in my view no need but another spark has previously flagged this up your thoughts please

Can those tables etc. introduce a potential to the installation ie. are they an extraneous-conductive parts? The answer will almost certainly be 'no' but you can confirm it with the 22kOhm test.
 
As IQ says do the IR test and if above 23KΩ then not considered an extraneous-conductive part and doesn't need bonding to the MET. I would be very suprised if they are connected to 'earth' though but you never know!!

Bonding it when it doesn't need to be bonded introduces a potential 'earth' path for a fault current which is what you dont want!
 
It is deemed 10mA is 'safe' so 230V/10mA = 23,000Ω.

Some prefer to use 5mA, 46,000Ω.

However, the measurement is unlikely to be between a few ohms and meg(a)ohms.
If you get 23,001 something is amiss.
 
10mA is a "safe current" that will not be likely to kill anyone. Therefore if there is a resistance of 22000 ohms on a 230V supply 10mA will flow.
The resistance of the human body on average is about 1000 ohms so you get either 22k or 23k or 21k as a safe resistance for a piece of metalwork to earth as it will not cause harm due to electric shock.

Edit:Too slow!
 
you set your mft to IR test, 500V. test from the suspect metalwork to the MET. if the reading is > 22 kOhms, then there can only be a current of 10mA through a body in a fault situation. 230V/ 23kohms = 10mA. so non-fatal.
 
Unless you have a pacemaker then 10mA won't kill you but you'll be dancing like Michael Jackson on a bad day:):rofl::party::rockon:
 
set your mft to IR test, 500V. test from the suspect metalwork to the MET

Taking care, if you think it might be an extraneous conductive part, that you don't end up testing the insulation resistance of someone who happens to be holding a different bit of it somewhere else in the building!
 
Taking care, if you think it might be an extraneous conductive part, that you don't end up testing the insulation resistance of someone who happens to be holding a different bit of it somewhere else in the building!


now that would be taking all the fun out of IR testing. imagine the master of the house giving the maid a table ender in the kitchen and you wallop 500V up them. what fun!.
 