I generally enjoy a tripping RCD but not this time!
Yesterday I fitted a spur. I drilled through the wall (at a slight angle) and fitted a single socket the other side of the wall from the socket I spurred from. As simple as that.
I was in a rush so I took a Zs which was 33 and planned to return to do the rest of the tests. However the client called a few hours ago to say her electrics were tripping. I went around and tested. IR N-E 250v = 12Mohms, N-E 500v 0.1Mohms. Ramp test 26mA. The IR tests were between the earth bar and the neutral bank were the RCD was tripping.
I also clamped the main earth and whilst the kettle was boiling it went up to 28mA. Kettle not boiling 6mA. But... the RCD was tripping when the kettle was not even plugged in.
The 0.1Mohms at 500v just makes me think a surge protection device is plugged in and this is a red herring as this result would not trip an RCD.
It must be my new socket?? But it's just though the wall and out the other side. I did go at a slight horizontal angle and there is a telephone socket that I may have gone through but I'm clutching at straws would going through a telephone cable have any effect? It's got to be my fault as this has only happened since I put the socket in.
Lastly, I moved all other circuit breakers on to the other RCD (which luckily only had one existing MCB), that RCD remains fine so I know the fault is on the same circuit as my new socket.
Sorry for this rather rambling post, I've only just got back from her house and I am done in!
Yesterday I fitted a spur. I drilled through the wall (at a slight angle) and fitted a single socket the other side of the wall from the socket I spurred from. As simple as that.
I was in a rush so I took a Zs which was 33 and planned to return to do the rest of the tests. However the client called a few hours ago to say her electrics were tripping. I went around and tested. IR N-E 250v = 12Mohms, N-E 500v 0.1Mohms. Ramp test 26mA. The IR tests were between the earth bar and the neutral bank were the RCD was tripping.
I also clamped the main earth and whilst the kettle was boiling it went up to 28mA. Kettle not boiling 6mA. But... the RCD was tripping when the kettle was not even plugged in.
The 0.1Mohms at 500v just makes me think a surge protection device is plugged in and this is a red herring as this result would not trip an RCD.
It must be my new socket?? But it's just though the wall and out the other side. I did go at a slight horizontal angle and there is a telephone socket that I may have gone through but I'm clutching at straws would going through a telephone cable have any effect? It's got to be my fault as this has only happened since I put the socket in.
Lastly, I moved all other circuit breakers on to the other RCD (which luckily only had one existing MCB), that RCD remains fine so I know the fault is on the same circuit as my new socket.
Sorry for this rather rambling post, I've only just got back from her house and I am done in!