I generally enjoy a tripping RCD but not this time!

Yesterday I fitted a spur. I drilled through the wall (at a slight angle) and fitted a single socket the other side of the wall from the socket I spurred from. As simple as that.

I was in a rush so I took a Zs which was 33 and planned to return to do the rest of the tests. However the client called a few hours ago to say her electrics were tripping. I went around and tested. IR N-E 250v = 12Mohms, N-E 500v 0.1Mohms. Ramp test 26mA. The IR tests were between the earth bar and the neutral bank were the RCD was tripping.

I also clamped the main earth and whilst the kettle was boiling it went up to 28mA. Kettle not boiling 6mA. But... the RCD was tripping when the kettle was not even plugged in.

The 0.1Mohms at 500v just makes me think a surge protection device is plugged in and this is a red herring as this result would not trip an RCD.

It must be my new socket?? But it's just though the wall and out the other side. I did go at a slight horizontal angle and there is a telephone socket that I may have gone through but I'm clutching at straws would going through a telephone cable have any effect? It's got to be my fault as this has only happened since I put the socket in.

Lastly, I moved all other circuit breakers on to the other RCD (which luckily only had one existing MCB), that RCD remains fine so I know the fault is on the same circuit as my new socket.

Sorry for this rather rambling post, I've only just got back from her house and I am done in!
 
The change between 250 and 500 sounds like surge protection but you would need to confirm. You haven't made the error of test after I have made the alteration. From what you have done it sounds odd although not impossible you have caused the problem but it could be sheer coincidence.
 
Last edited:
Westward.. I was in a rush and Im embarrassed to say I have not followed the correct testing procedure this time. I'm snowed under and rushing and that's when mistakes happen! Ive cancelled my job tomorrow and am going back to the lady.

Murdoch.. I agree, however would I not be getting some poor IR readings if I'd nicked a neutral with the socket screw?

I shall disconnect tomorrow and see. But why no faulty readings!!!??

PS. When I moved the suspected faulty circuit to a different RCD, that RCD then tripped so I know it's not a faulty RCD.
 
Pre tests may not have shown anything and as you say if surge protection is causing low readings these should not result in nuisance tripping. Could be the case of coincidence that your work is fine but something else has suddenly decided to trip the rcd.
 
Hi HHD.. did you IR individual circuit or global? You need to split the socket circuit with the fault down bit by bit until you find the cause of the 0.1 Mohm fault reading..

Did you unplug all appliance on that socket circuit?
 
Assuming it is not a coincidence and the fault is on your new socket then the obvious thing is to disconnect the new spur at the supplying socket and see if the RCD still trips.
If it stops tripping then you only have one spur cable and one socket to inspect and test.
The RCD itself might cause a low IR reading at >250V.
Test the socket circuit on its own to narrow down the IR fault on that circuit.
I hope that tomorrow you will be less stressed and will easily identify the fault.
Good luck for a rapid resolution.
 
Hi bud,i will volunteer to go out tangentish...

Is this a new customer? Sometimes a wily customer,with a persistent,previously attempted tripping issue,may pay for a simple,straightforward job,to get what is in effect,a "fixed-price" solution;)

Or...was that failing kettle,faulty,or did it's load,push a fault on that circuit? Try it on another circuit.

Also,has this rcd tripped during your visit? Regardless of readings,have you witnessed it trip?

...Is the customer a lonely spinster,who has noticeably applied additional make-up,and a frock,from her clubbing years? :rolleyes:
 
Instead of clamping the main earth or even the circuit earth during a live leakage current test, rather clamp the live and neutral together, that will give you a reading of all leakage current including parallel paths instead of just the leakage returning on the circuit earth.
 
My brain feels clear again after a nights sleep!

Thanks everyone for all the ideas. I shall return with the new ammunition and find that fault!!:)
 
Hi bud,i will volunteer to go out tangentish...

Is this a new customer? Sometimes a wily customer,with a persistent,previously attempted tripping issue,may pay for a simple,straightforward job,to get what is in effect,a "fixed-price" solution;)

Or...was that failing kettle,faulty,or did it's load,push a fault on that circuit? Try it on another circuit.

Also,has this rcd tripped during your visit? Regardless of readings,have you witnessed it trip?

...Is the customer a lonely spinster,who has noticeably applied additional make-up,and a frock,from her clubbing years? :rolleyes:

This struck a chord!
Some years back following a minor job the customer phoned back in a strop saying that the RCD was tripping regularly since our visit. During investigations the couples daughter dropped round and said, "Are you getting that sorted at last? Don't know how you've put up with it all this time, when did it start, Christmas wasn't it?"
Red faces and excuses followed.
 
Murdoch.. I agree, however would I not be getting some poor IR readings if I'd nicked a neutral with the socket screw?

Not necessarily ...... I was tracking a problem recently - the power would go off (and it was an up front RCD). IR showed noting odd

First visit just showed occasional tripping - next visit socket circuit tripped RCD as soon as it was reset ......... and then the IR was non existent L=E

Problem traced to socket where CPC and live were crossed in a 25mm back box and caused the problem ......

A new RCBO board was fitted a few weeks later... as the home owner had got 100% fed up with a single fault taking out the whole house...
 
when to a job yesterday. customer said ever time he put in a plug in to a surge protection extension that was feed from socket in the kitchen .he said it stopped working. found out the some of the sockets in the kitchen where extended from a j/b under a work surface neutral hanging out. a floating neutral . and hanging in mid air and using a lot of appliance's from that . and rcd protected not tripping
 