I am going to install an e.l.v fan in a bathroom.The nearest place i can site the transformer is beneath the bath.Which i interpret in the 17th is outside any zones if the side panel is accessable with a special tool i.e could be a screwdriver.I presume the transformer does not have to be ip rated as it falls outside protected zones.Can anyone confirm this is acceptable please?There is no other place i can situate the transformer that is accessable really.!!! and obviously safe.

Pretty obvious i know,but just to add primary side 230v & secondary 12v or there abouts:D
 
Last edited:
I can't speak about UK rules, but what I can say is that some factory-built baths come with one or several transformers and various similar electrical equipment already installed below the bath. Something pretty catastrophic would have to happen to the bath for the transformer to get wet under there. Barring other special rules, I wouldn't hesitate to place it there.
 
Last edited by a moderator:
I am going to install an e.l.v fan in a bathroom.The nearest place i can site the transformer is beneath the bath.Which i interpret in the 17th is outside any zones if the side panel is accessable with a special tool i.e could be a screwdriver.I presume the transformer does not have to be ip rated as it falls outside protected zones.Can anyone confirm this is acceptable please?There is no other place i can situate the transformer that is accessable really.!!! and obviously safe.

Pretty obvious i know,but just to add primary side 230v & secondary 12v or there abouts:D

absolutely - its outside the zones

I am just fitting a supply for one of these space age 'steam' showers, with a radio, lights, MP3 connection (and i am not sure but i think its got SatnaV)

so its a socket under the showerbasin - no problems:)
 
>>Why can't it go up in the loft above the bathroom?>>
What if the bathroom is on the ground floor -;)
 
Why the need to have it so close?
Read the instructions first bet there is a table giving distance between fan & transformer & csa of cable to be used over said distance.

Xpelair LV100 I've just firstfixed the tranny is in the airing cupboard some 12 meters away from the fan itself.
 
Cheers lads thats what makes this site so good,i appreciate everyone taking the time to answer my question all noted and taken on board.Should have said couldnt mount tranny in loft as it is a flat& concrete ceiling.Suggestions about putting near triple pole isolator,which i normally fit outside bathroom above door,would this not look a bit ugly and obtrusive?? without sounding ungrateful for the idea.
 
I have on two occations put them in the stud wall beside the TP isolation switch above bathroom door, then installed a small white plastic access hatch that I got from B&Q.
 

Reply to transformer beneath bath in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock