If they are supplied with the gear, then I'll fit em, however none of the gear I'm supplied with comes with earth straps. In fact, as far as I'm aware, only ladder rack joiners come with earth straps as standard.

all of the tray and trunking we use comes with steel joiners, and I fit them, and always ensure they are tight.

regarding specifications, a lot of company specs are over engineered. Our spec calls for all electrical equipment to have voltage labels, which is above and beyond BS7671 (unless over 230v to earth, which 99% of LV installations are not).
we also have to link from the banjo of the load end of a cable to the nearest metalwork.
this is also above and beyond BS7671.

just because you see it in specs, it doesn't mean they we have to follow the same rules, when you can prove that the alternative is just as safe, and more economical.
 
just because you see it in specs, it doesn't mean they we have to follow the same rules, when you can prove that the alternative is just as safe, and more economical.

You can do whatever you wish to do, and i'm sure you will, but if a specification calls for them, (or working on a project of mine) they Will go in... lol!!
 
I agree its a waste of time using straps unless you make a bad job of connecting, and powder coated was the only time i have seen links supplied with trunking you have to buy them as a extra nowadays, also if you look the 90 and T bends only have one or two holes to connect between the trunking and the bend most don't have couplers between a bend and the trunking and its self so that means you would have to drill a second hole to install & connect a link yes ?
 
You can do whatever you wish to do, and i'm sure you will, but if a specification calls for them, (or working on a project of mine) they Will go in... lol!!

And here was me thinking you weren't one to follow dogma.
Sorry E54 but we’ll have to agree not to agree on that one.

I will add it would be a rare occasion where I would be mounting trunking or tray against a brick wall. When we did our normal practice would be construct a welded frame in the workshop with everything drilled to suit before hand.
 
And here was me thinking you weren't one to follow dogma.
Sorry E54 but we’ll have to agree not to agree on that one.

I will add it would be a rare occasion where I would be mounting trunking or tray against a brick wall. When we did our normal practice would be construct a welded frame in the workshop with everything drilled to suit before hand.

Depends on the dogma!! lol!!

As i have always worked primarily on highly spec'd projects, it's almost second nature to me to use copper straps across tray and trunking installations. Same goes with flexible earthing straps across isolating flexible joints on A/C ducting.
 
Depends on the dogma!! lol!!

As i have always worked primarily on highly spec'd projects, it's almost second nature to me to use copper straps across tray and trunking installations. Same goes with flexible earthing straps across isolating flexible joints on A/C ducting.

I'll not disagree with bonding flexible joints. Ducting depends on its construction.

The companies I've worked for were all blue chip so money hasn't really been an issue, just what's required.
 

Reply to tray bonding in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

NICEIC Certification Scheme Getting accredited to
Looking for some advice regarding joining a CPS. I've been in the electrical industry in various roles for nearly 10 years. I started my...
Replies
15
Views
1K
Hi all Regarding bonding of cable tray and basket. Is basket required to be bonded if only data cables installed on it ? plus bonding cable tray...
Replies
28
Views
8K
Hi all Just a question on segregating of cables and other services. I have a tray route to install for a small cafe and going to be supplying...
Replies
0
Views
984
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
565
Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
822

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock