Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused isolator switch. This has been replaced with 25mm tri rated cable. Looking at the specs for BS 6231 I can see the conductor can take 136 amps. Motors are 37kw. Is there anything I’m missing. How do you apply grouping factors for a panel running a single motor or is grouping factors not applied?

Thanks guys
 
Treat it as any other trunking for grouping factor. Consider ambient temp on panel and how often the load will be starting and stopping
If it’s 3 phase 3xsingle core and control circuits within the trunking how does this related to how many loaded circuits? Found this in bsen 60204-1
 

Attachments

  • image.jpg
    413.1 KB · Views: 2

Reply to Tri rated cable and grouping factor in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data...
Replies
6
Views
3K
So I just started out recently and I’m struggling with what to price myself at. It’s worth noting I live in the east London area and I’m looking...
Replies
12
Views
589
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...
Replies
5
Views
1K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock