RCD trips between 2 to 4, and again at 11.

Can't be too difficult to trace the cause surely.

Ridiculously easy by the sounds of it.

Bloke also originally put that the mcb was tripping and then said rcd and blamed auto correct.
 
@ the OP - WHAT happens at these times? We are not there. We rely on information you provide us.

Happy to help. Even happier when we get feedback on how the issue was resolved.

(Just something to think about if you want to get the best out of the forum).

Voltz (No.1 Grammar police).
 
@ the OP - WHAT happens at these times? We are not there. We rely on information you provide us.

Happy to help. Even happier when we get feedback on how the issue was resolved.

(Just something to think about if you want to get the best out of the forum).

Voltz (No.1 Grammar police).

Did we ever get to the bottom of that bloke who found voltage in a shower waste tray?
 
I've measured neutral to earth and have found that all are have a high resistance bar the downstairs lighting circuit that that has a reading of 0 ohms./QUOTE]

In which case, I'd get that IR sorted. It may not be the main cause of the problem, but it's not going to help in the case of an RCD tripping.

What's the actual resistance value (measured on a low ohms range if necessary)?
 
Sorry What I should have posted was "I say that question has already been asked? hasn't it?" jolly good lol
 
First 0 ohms was high resistance
Then 0 ohms was low resistance
0 ohms will be zero resistance,
ie no resistance at all, there's not a superconductor in the circuit by any chance is there? Lol.
 
If it happens that regular and you have not test equipment. Why not isolate each circuit untill you find the suspect circuit at fault ?
 