Hi all, went to look at a job today. All was wanted was a fcu for a new boiler in a shower block(shed!) on a caravan site. Shower block is fed in 2.5 swa, 20m underground from main supply. TT, 100ma, 6A. Load is for 3 lights only. The problem Ive got is bonding the water and lpg in shower block. Would intalling an extra rod at shower block and conecting all earth together resolve my prolem? 1 unhappy caravan site owner if ive got to dig up 20m trench for earthing! But if its gotta be done, its gotta de done. Advice appreciated. Thanks.
 
Struggling to picture this in my head (maybe it's the takeaway i've just had, yum)

So, you're saying there isn't a CU/DB in the block at all, the cable is fed from the main supply underground straight to the 3 lights? Thus, the 6A breaker been away from the shower block at source?
 
Not sure why im bothering picturing it anyway, just rod the showerblock like you've said.

Then obviouslly test too make sure readings are glorious.
 
See you're location is Bala - was there a few years ago when we decided to give whitewater rafting a go, got kicked off the caravan and camping park for wheelspinning my van across the land.

Probably the same place as you're at haha.
 
You yorkshire lads ehy!ha. Site is 20 miles south, I doubt its the same 1! Set up pretty much as you have described. Intalling the fcu is straight forward, its just providing MEB for the shower block really.
 
See you're location is Bala - was there a few years ago when we decided to give whitewater rafting a go, got kicked off the caravan and camping park for wheelspinning my van across the land.

Probably the same place as you're at haha.

might be worth looking for an earth rod now you know about markc123s driving
 