A

austin

Hi guys i have an old house with a TT system. The meter etc is at he front door while the gas and water is at the rear (quite common i believe) Must be a distance on ten meters or so. There is no bonding between the two at present. Do i have to run an earth all the way to the gas and water? There is a radiaror close to the CU can I bond to this and bond gas and water together as an alternatine??
 
No...you must run a main bond to the gas and water from the MET ,which for TT can be 6.0mm....but I'd run a 10.0mm so if the system is ever changed to TNCS there will be no need to upgrade.
 
Hi guys i have an old house with a TT system. The meter etc is at he front door while the gas and water is at the rear (quite common i believe) Must be a distance on ten meters or so. There is no bonding between the two at present. Do i have to run an earth all the way to the gas and water? There is a radiaror close to the CU can I bond to this and bond gas and water together as an alternatine??


You jest, surely???
 
Ok I will do the run then, its not going to be easy but i want to do it right. Modern houses are much easier, Our water and gas come down the back lane and feed the back of the house while our electric comes to the front.
Cheers
 
You can run a single earth from your MET at front of house to gas / water services at rear. This can be terminated onto both services as long as the cable is unbroken at 1st service connection.
 
Sintas right, if you don,t break the cable , we on a very few occasions have double the 10mm over and crimped it into 1x lug, and then on to the other, but normally we run 2x 10mm cables and write gas and water in con/unit with an indelable marker.
 
just out of curiosity, why can you not break the cable at the connection to 1st service? Surely its all connected at the same point anyway? I've been told not to and have never seen it done but nobody has ever actually explained why?

cheers
 
Because plumbers/DIYers often remove main bonds and cant be trusted to reconnect them properly,especially two separate conductors. At least if the wire is continuous if i'ts removed at one service it wont be lost at the other as well.
 
Would it be a possibility to put down a seperate rod at the rear of the house and bond to those? I assume it`s probibly a nono, but worth checking. richard
 