Engineer54
Very nice, I don't have nerves of steel like you so I usually dig at least 500mm first with a spade, I've hit too many drains and water pipes in my time so I'm a bit skittish.
Just out of interest don't you get a 2.4 meter rod which would save the need for a coupler? Also did you get 15ohms just testing the rod or was that after it was connected and possibly with parallel paths? If it was just the rod then that's very good ground, we usually need multiple rods or around 10-15 meters depth where I am to get an impedance that low![]()
I'm with you here Marvo, ....i've never actually ever used a 1.2m rod in my life!! lol!!
Well as you have stated many times here, your driving rods into a sand based soil, and by the sound of the depths you have to go, all the sulphates etc, must have been well and truly washed out of that sand too... lol!!