I am curious, and I am not knocking anyone here or their respective efforts, but a couple of questions;
- Glennspark, did you take a reading from the ROB to a Test spike or from the rod to the earth point of the installation?
- When installing rods does anyone actually test them correctly with a rod tester?
- When doing the testing, does anyone actually have spare rods and joiners in case they need to go down deeper?
- What is the minimum reading you would personally accept?
When I have ever installed rods personally, or been on a job where they were installed, I have ensured that they were tested properly as they were inserted into the ground and that more rods were added until the reading achieved was an absolute minimum of 10Ω, however I have never stopped as soon as I get this value, I will add rods until I get a stable return. Over the years I have found that about 4 rods will get you into the 1Ω range (+/-0.5Ω), and a fifth rod will easily achieve lower than 1Ω, and at these depths we are talking stable return paths.
As said, I am not having a go at the technique anyone uses, I will always attempt to get the reading as near to 1Ω as possible because I hate the idea of being reliant on the RCD, like all devices they fail and the ground state within about 2.5m of the surface is too impacted by the above surface environment, man made influences and the weather/climate.