Glenn why 21?....why not go the whole way and get a TN value?....isnt 21 just a figure plucked out of the air the same as 200....or 100? And assuming you install a TT system are you really going back to site to 'monitor' it over a period of time? Why not just get it to sub 1 ohm and go home and forget it?
iI you are achieving TN values of Ra then good onya. You are not happy to rely on an RCD and therefore insist on a reading which will make that possible. Personally I am happy to rely on an RCD for the small scale TT systems I install and therefore see no need for TN values,the reason being that in the 35 years I,ve been a spark I've yet to hear of an incident on a typical UK TT installation which would have been prevented with a lower Ra . My issue is with those who are not achieving TN values and yet scorn reliance on RCD's,when the values they quote as being aimed for still rely on an RCD.I am curious, and I am not knocking anyone here or their respective efforts, but a couple of questions;
- Glennspark, did you take a reading from the ROB to a Test spike or from the rod to the earth point of the installation?
- When installing rods does anyone actually test them correctly with a rod tester?
- When doing the testing, does anyone actually have spare rods and joiners in case they need to go down deeper?
- What is the minimum reading you would personally accept?
When I have ever installed rods personally, or been on a job where they were installed, I have ensured that they were tested properly as they were inserted into the ground and that more rods were added until the reading achieved was an absolute minimum of 10Ω, however I have never stopped as soon as I get this value, I will add rods until I get a stable return. Over the years I have found that about 4 rods will get you into the 1Ω range (+/-0.5Ω), and a fifth rod will easily achieve lower than 1Ω, and at these depths we are talking stable return paths.
As said, I am not having a go at the technique anyone uses, I will always attempt to get the reading as near to 1Ω as possible because I hate the idea of being reliant on the RCD, like all devices they fail and the ground state within about 2.5m of the surface is too impacted by the above surface environment, man made influences and the weather/climate.
1)measurement was taken as a Ze....the rod including any main earthing conductor (in this case 10meters of 10mm G/Y)
2)all my MFTs all have 2 wire, 3 wire and specific ground resistance ability...i need to get the test leads & spikes for this
3)In this case I was left with 2 rods...had it been one of my own jobs i would have certainly got three....as i have advised before in here
4)well....certainly not 200 ohms.....nor 100 ohms for that matter...lol....definately no more than 21....and then monitor it to see how much that drops...if not enough then send another rod in...but you really should be acheaving better than 21....
Glenn why 21?....why not go the whole way and get a TN value?....isnt 21 just a figure plucked out of the air the same as 200....or 100? And assuming you install a TT system are you really going back to site to 'monitor' it over a period of time? Why not just get it to sub 1 ohm and go home and forget it?