ChrisElectrical88
I think I will tell him to leave it disconnected and get up there on Friday to check it out myself. It's RCD protected anyway due to it been a special location.
doesn't make sense. if it's TN-S the Ze should be below 0.8. and to give a PSC of 79KA, it would be 0.003
If it is on a livestock holding , it would more than likely need to be TT anyway .
I assume he means PEFC not PSCC.I thought the 79 amps was okay for pefc Richard, but isn't that low for pscc?
He's normally spot on to be fair to him. Don't know what happened with that one!