PROBLEM ! TT SYSTEM
TESTING FOR Ze ,INCOMER SWITCHED OFF EARTH DISCONNECTED FROM CU ,USING EARTH LOOP IMP TESTER .for earth electrode being a spike .Ub>UL reading
phase neutral + earth 246v
phase to earth 268v
N to earth 52 v sometimes higher than that
im in frame of mind that the meter will not work as out of range with N-earth above 50v but need a solution .as i cant evaluate max Zs for mcb's rccd .
Rccd will not test either to make matters worse .

additional earth spike put in but to no avail .
got same reading at origin meter 50mtr away .
any suggestions as i have never had this problem in 28yrs so never knew where to look and any further work at this installation is on standby till satisfied with this problem .
I can't speak to the elcectricity provider as i dont speak Spanish but the principals are the same as i have a TT system in my home and tests OK and in its limits .
any advice would be helpful

i question my competence ,am i losing it ? any old spark out there with some knowledge .
 
Last edited by a moderator:

Reply to Tt system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock