I've got a RFC that I need to split into two 20A radials.

I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).

I've had a little look online and I think that it might be 23A (before taking other derating factors into account).

Can anyone verify this?
 
23A would seem suitable to me as this figure is ref method B for 2.5mm PVC/PVC cable from table 4D2A. As the other values from this table are congruent with table 4D5 then I would say you're good to use this table.
 
23A would seem suitable to me as this figure is ref method B for 2.5mm PVC/PVC cable from table 4D2A. As the other values from this table are congruent with table 4D5 then I would say you're good to use this table.


Nice one, thanks :thumbsup:
 
I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).


that's because the IET assume that cables run in conduit are singles.
 
I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).


that's because the IET assume that cables run in conduit are singles.
It does give method B for multicore pvc pvc in trunking which is the closest.
Methods 8 and 9 from appx 3. Or appx 4 maybe, I forget.
 
I'm sure I'm not the only one who has put twin and earth in trunking or even conduit before. :tearsofjoy:

They need to update the book
It's never been included because containment is for non-sheathed singles. Insulated and sheathed cable is designed to have its own mechanical protection (the sheath) where risk of impact is low.
 
It's never been included because containment is for non-sheathed singles. Insulated and sheathed cable is designed to have its own mechanical protection (the sheath) where risk of impact is low.
It is however extremely common to install pvc sheathed cables inside mini trunking or where they come into a CU and the cables are trunked above 50x50 mm pvc etc.
 
It is however extremely common to install pvc sheathed cables inside mini trunking or where they come into a CU and the cables are trunked above 50x50 mm pvc etc.
I'm not disputing any of that - just trying to explain why there never have been (and likely never will be) reference methods for this type of thing.
 

Reply to Twin & Earth CCC in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock