I've got a RFC that I need to split into two 20A radials.

I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).

I've had a little look online and I think that it might be 23A (before taking other derating factors into account).

Can anyone verify this?
 
23A would seem suitable to me as this figure is ref method B for 2.5mm PVC/PVC cable from table 4D2A. As the other values from this table are congruent with table 4D5 then I would say you're good to use this table.


Nice one, thanks :thumbsup:
 
I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).


that's because the IET assume that cables run in conduit are singles.
 
I've looked in the BBB but it doesn't state the current carrying capacity of twin and earth in surface mounted trunking (reference method B).


that's because the IET assume that cables run in conduit are singles.
It does give method B for multicore pvc pvc in trunking which is the closest.
Methods 8 and 9 from appx 3. Or appx 4 maybe, I forget.
 
I'm sure I'm not the only one who has put twin and earth in trunking or even conduit before. :tearsofjoy:

They need to update the book
It's never been included because containment is for non-sheathed singles. Insulated and sheathed cable is designed to have its own mechanical protection (the sheath) where risk of impact is low.
 
It's never been included because containment is for non-sheathed singles. Insulated and sheathed cable is designed to have its own mechanical protection (the sheath) where risk of impact is low.
It is however extremely common to install pvc sheathed cables inside mini trunking or where they come into a CU and the cables are trunked above 50x50 mm pvc etc.
 
It is however extremely common to install pvc sheathed cables inside mini trunking or where they come into a CU and the cables are trunked above 50x50 mm pvc etc.
I'm not disputing any of that - just trying to explain why there never have been (and likely never will be) reference methods for this type of thing.
 
I'm not disputing any of that - just trying to explain why there never have been (and likely never will be) reference methods for this type of thing.
I’m just saying that maybe it should be included in the relevant table for flat pvc pvc twin and earth cables as it’s a common situation. Or maybe just refer to the other table.
 

Reply to Twin & Earth CCC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, The current carrying capacity tables in the BS 7671 for twin and earth cables are only for buildings that have thermal insulation. I'm...
Replies
48
Views
4K
I've been told I need to upgrade the main earth bonding to 16mm. The consumer unit is on the wall adjacent to the externally mounted incoming...
Replies
30
Views
4K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
457
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock