Discuss Type A RCDs Vs Type AC in the UK Electrical Forum area at ElectriciansForums.net

The reason we should install DP (switched neutral) RCBOs in a TT system is only when an up-front RCD (100mA S Type) is installed so that we achieve selectivity and avoid nuisance tripping from a neutral - earth fault which would then trip the up-front RCD in fault conditions.
 
How many of us own the appropriate DC RCD tester to test Type A RCDs?

You'd hope everyone who needs one does, though this is unlikely to be the case.

My MFT (Megger 1730) is capable of testing types AC, A and B RCDs and I think most common testers are capable of AC and A type.
 

Reply to Type A RCDs Vs Type AC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
675
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
676
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
618
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.