stidge
Hi, just had quick look at job, 2 x heating matts 1 x 3600w - 16a and 1 x 3450w 15a. They will be run to two seperate FCUs and thermostats, !!No new ccts can be installed, in your opinion lads would it be ok to take both off ring main( allowing for diversity) with both FCUs fitted with 13 Amp Fuse ?? Also the Main Switch is an ElCB which I believe are no longer viable ? Would you Fit RCD FCUs ?cheers for all input
fused down...
come on, what do you think?
- - - Updated - - -
RCD fcu`s is the way...
Forgot to say will be two seperate rings, agree new cu is the way but expense blah blah, need to visit job again think I will go for rcdfcu's. thanks for input
ask yourself this:
1, is ufh a fixed appliance?
2. is each mat > 2.2kW?
if answer is yes to both, then separate circiuts required. end of.
only way to do that witout a new CU is to henley block tails into a 2 way sub CU with RCD protection ans a 20A breaker for each mat.
and to be fair by the time you add the price of 2x rcd spurs ( not to mention how good they look) you are nearly at the price of a new cu anyway.
You have to forget this "it has to be cheap" solution crxp. Outline the solution and the best way of resolving it.
And also how long would the 13A fuse hold for on the 16A mat?
Thanks tel,Murdoch and lister, have taken all comments on board and I'm going to tell them new circuits and new board or no go ! Rather be sure than fit and **** up ! Cheers
tell 'em it's like trying to pull a 2 ton caravan with a 1.0L corsa. they either get a more powerful car or can't go uphill.