I would fully support that assessment, a good continuous, correctly installed conduit system, is a more than adequate means of CPC..
 
......and a knowledge of the type of installation to be tested/inspected.

Key words when undertaking periodic inspections.
 
Bit late to join the party, but you did test the right CPC's ? Very easy if a dedicated CPC is installed for someone before you to not connect in the same sequence of the earth bar as you think, and if you have several circuits coming into the board via one conduit it is easily done.

I would make 100% sure you have the right 2 CPCs for the ring final.
 
if its in conduit you are also have fly leads on lighting circuits and other rings or radial circuits are you going to dissconect all of them as well because you will be on about 2p an hour
 
Seeing as the last reply to this thread was in 2011 I think it is safe to say the op will have resolved any problems he had, Thread closed.
 