Don't get caught in the Traffic Warden mentality when doing a EICR ie you have then pen the uniform the training and your going to dictate what happens if there is one thing you need to learn is that your are not BG you cannot walk in to a property condem it switch and lock off the supply and walk out the door just do your job and see if it passes the tests and yes by all means recommend but if you cross the line and say this needs replaced or else well thats fraud So remember test and put down Satisfactory or Unsatisfactory depending on the outcome of the test.
 
Don't get caught in the Traffic Warden mentality when doing a EICR ie you have then pen the uniform the training and your going to dictate what happens if there is one thing you need to learn is that your are not BG you cannot walk in to a property condem it switch and lock off the supply and walk out the door just do your job and see if it passes the tests and yes by all means recommend but if you cross the line and say this needs replaced or else well thats fraud So remember test and put down Satisfactory or Unsatisfactory depending on the outcome of the test.




I would never say something NEEDS replaceing without properly inspecting and testing it first!!!
I will always recommend something be done if I feel it neccassary. The question was really would you test it if you came across it?? I personally wouldn't and I would RECOMEND it be removed and rewired. But that is up to the customer.
 
Yep don't get caught out like the clown who told a landlord he had to have a RCD CU if renting a property Landlord got ALL of his money back ie cost of EICR, Cost of any repairs and cost of replacing the CU so yes recommend but don't get power crazy
 
I would never say something NEEDS replaceing without properly inspecting and testing it first!!!
I will always recommend something be done if I feel it neccassary. The question was really would you test it if you came across it?? I personally wouldn't and I would RECOMEND it be removed and rewired. But that is up to the customer.

Why wouldn't you test a VIR installation if your conducting a full EICR?? A full EICR would call for the inspector to remove and inspect a certain number/% of wall and ceiling accessories, so you should be able to see if any insulation degradation is present or not. As for your statement about not testing a VIR installation, i really can't understand that approach at all, it's all part of what you're being ''PAID'' to do!!!!


Look in an ideal world all old wiring should be replaced as a matter of course, but we live in the real world of recessions and the like, where that ideal is not always possible. Of course if during the EICR inspection it becomes apparent that the insulation of old cables is falling apart willy nilly, then fine you have no alternative but to code it as necessary, which will undoubtedly lead to the requirement of a full or partial rewire...
 
Yes thats the "inspection" bit. Sometimes things don't need to pass a test they're so bad!
 
a bit similar with a car/van MOT. if the tester considers the vehicle to be unroadworthy, he can refuse to test it: obviously , it would be a fail.
 
Why wouldn't you test a VIR installation if your conducting a full EICR?? A full EICR would call for the inspector to remove and inspect a certain number/% of wall and ceiling accessories, so you should be able to see if any insulation degradation is present or not. As for your statement about not testing a VIR installation, i really can't understand that approach at all, it's all part of what you're being ''PAID'' to do!!!!


Look in an ideal world all old wiring should be replaced as a matter of course, but we live in the real world of recessions and the like, where that ideal is not always possible. Of course if during the EICR inspection it becomes apparent that the insulation of old cables is falling apart willy nilly, then fine you have no alternative but to code it as necessary, which will undoubtedly lead to the requirement of a full or partial rewire...

I understand that its my responsebility, as the inspector to test accordingly but we all know that the majority of this cable is way past its best! And as I said earlier, Ive had a bad experiance with this stuff just by brushing aside a few cables. I had to then fix the faulty cable at my own cost, as it was me that damaged it (in the customers eyes).lol

I will always inspect the cable but Ill try and avoid testing it and recommend it be replaced. For all I know, testing it could disturb the insulation and leave it in a bad state than it was.

I'm not knocking any one who would test it regardless but I wouldnt.
 
i see your concern. it's sometimes a difficult call. my thoughts would be first to see the condition of the VIR in the CU as this can be visually inspected without disturbance. if that looked OK, then i'd be tempted to open an accessory, generally an upstairs socket so that if the cable there was in poor condition, it'd not be too much of as job to cut and joint under the floor. if insulation was crumbling, then i'd code it from visual. no need for an IR test then.
 
i see your concern. it's sometimes a difficult call. my thoughts would be first to see the condition of the VIR in the CU as this can be visually inspected without disturbance. if that looked OK, then i'd be tempted to open an accessory, generally an upstairs socket so that if the cable there was in poor condition, it'd not be too much of as job to cut and joint under the floor. if insulation was crumbling, then i'd code it from visual. no need for an IR test then.


I suppose it all boils down to experiance. Ive not come across it that often and when I have, its been a right mess, falling apart as soon as Ive reomve the fitting!!! And from reading numerous things about the stuff, at the moment, In my experiance, I personally wouldnt want to test it. But maybe if I come across it more often in the future and it looks ok and my experiance of the stuff grows, I may give it a test...never say never.lol

I dont think im the only one that wouldnt test it....hopefully!!lol
 
Its similar when someone comes on the forum saying my God they are using the conduit as an earth so as a 14th edition electrician I just don't see a problem so as said do the EICR put down your results give your recommendations and thats it just dont be tempted scare the life out of the customer who may phone say their dad who will say well you have been living with it for the past 10 years and you have not died yet.

Me I prefer to leave BG to do the scare tactics
 
Its similar when someone comes on the forum saying my God they are using the conduit as an earth so as a 14th edition electrician I just don't see a problem so as said do the EICR put down your results give your recommendations and thats it just dont be tempted scare the life out of the customer who may phone say their dad who will say well you have been living with it for the past 10 years and you have not died yet.

Me I prefer to leave BG to do the scare tactics


Ive come across a few installs that has used the conduit and trunking as a cpc, even in some domestics. When Ive tested the Zs, the readings have been good, even when some of the trunking/conduit looks a bit batterd.lol

And I know all about the dealings of BG.......I went to a customers house a while back to quote for adding some sockets. Having a look round, I noticed she had a new board fitted....dual rcd 10 way....she only had two circuits...lights on one rcd and sockets on the other!!! What a waste. Still, at least the got the discrimination right!!lol They charged her nearly £600!!!
She was fairly old and I believe they used scare tactics, although I cant confirm this.lol
 
If I seen vir I would stop immediately don't desterb as the insulation could start to crumble recommend a rewire if the customer doesn't want to no walk away


Basically to take that position, is the difference between an experienced electrician and one that is not!! If the insulation shows no signs of degradation, taking that position is just pure scaremongering!!
 