Looking to see where I went wrong and see why I made a mess of things.

I was asked to install a Hive onto a Vokera Vision 30C combi boiler.

I turn up, 3 core from FCU to hive receiver (LNE) and then a 5 core flex from the receiver to the boiler (LNE and 1&3 from inside the receiver) and inside the boiler the standard LNE and take the link out of the connector block on the left hand-side and connect 1&3 to the connector block.

Turn on the FCU and everything is fine. I call for hot water and bang, MCB trips, PCB board scorched. No fuses inside on the PCB blown though.

Can anyone explain if possible the heck I did wrong? I am expecting a rough time, but I want to understand where I went wrong so don’t just the p**s out of me.

I now have to pay for this to be fixed but I want to know what I did wrong. I’m even brave enough to admit I have to pay another guy to fix it now.

I have added a picture of the pcb board before I wrecked it.
 

Attachments

  • Vokera Vision combi boiler 9508F768-9CAA-48F5-834E-60654346A590 - EletriciansForums.net
    9508F768-9CAA-48F5-834E-60654346A590.jpeg
    403.2 KB · Views: 32
If you have wired it as described then the only way I can see why this occurred is you have used a 2 channel Hive receiver and put 240v up the 24v control side

I'm a bit confused by the call for hot water and it went bang when this is a combi boiler, exactly how did you call for hot water was this by turning a hot tap on
 
Can you show a pic of the 'scorched' board too ?

So is the PCB definitely knackered and the boiler is no longer working ?
 
Don’t have the pic. But I have marked on the pic where the burnt marks where.

I disconnected my stuff, rigged it back up the original way and the boiler came back on. But no hot water or heating now.

Customer got proper p***ed off and called BG to come out. Which is fair enough I don’t blame them at all, especially when it’s been freezing. But I have tried to phone and text to see what they are saying and how much it’s going to cost and no reply from them now.
 

Attachments

  • Vokera Vision combi boiler DA3C2264-6A1B-44E1-B565-A2D1524DEF6D - EletriciansForums.net
    DA3C2264-6A1B-44E1-B565-A2D1524DEF6D.jpeg
    396.6 KB · Views: 24
I agree with UNG then... somehow you've managed to put 230v across the 'no volt' thermostat connection. Unless the boiler was already like that before you started ? How did you wire up the receiver ?

I managed to knock out a boiler PCB a few weeks ago... just by turning it off and back on again ! They can be delicate things !
 
I must have done something to blow the pcb. The receiver was LNE and 1&3 connections. I must have done or touched something that’s caused it. But was just to see if anyone knew offa hand with the little info I have or incase I was doing the connections wrong.

Out of curiosity Zerax, what did you do when you done that to the pcb? Did they manage to get heating and hot water still or what?
 
Out of curiosity Zerax, what did you do when you done that to the pcb? Did they manage to get heating and hot water still or what?
The board was as dead as dodo... even though there was power getting to it and both board fuses were intact. I was rather stressed, so I called a plumber mate of mine (well, when I say mate, I know him...) who calmed me down. He told me that it's remarkably common, especially on Alpha boilers ! Luckily the homeowners were very understanding and trusted me when I explained it to them, so I didn't get stung with repair costs. (£220 for a new PCB !). They actually seemed happy that it happened whilst I was there to diagnose the faulty board and swap it out for them !
 
Yup, turned the water on and bang.

Wasn’t a 2 channel hive receiver. I checked that before I took it out the box.
Did you check it after you took it out of the box, never assume what it says on the box is what is actually in the box
Don’t have the pic. But I have marked on the pic where the burnt marks where.

I disconnected my stuff, rigged it back up the original way and the boiler came back on. But no hot water or heating now.

Customer got proper p***ed off and called BG to come out. Which is fair enough I don’t blame them at all, especially when it’s been freezing. But I have tried to phone and text to see what they are saying and how much it’s going to cost and no reply from them now.
Can't find a decent wiring diagram for that boiler but the burn at the top of the board looks to be where the hive / thermostat ultimately connects via the smaller PCB on the left which looks to be the digital display in the diagram I have. As for the one at the bottom of the PCB the diagram doesn't give enough info to speculate on what caused that burn

When you were removing the Hive receiver did you do any analysis of the possible cause as other than a crossed connection or short on the 5 core it has to be the hive at fault.
Strangely with the single channel Hive no where in the instructions does it state the the control contact is volt free, although it does have common, heating off (nc) and heating on (no) connections which suggests it should be
I don't suppose you have the Hive unit and 5 core cable so you could test it to identify where the problem lies
 
Hive and boiler manuals attached if this helps.
 

Attachments

  • Hive_Thermostat_Installation_Guide-d5cf9bf693e5ad8f4d01a9e6edbaa46c9c2cbfbfbea01f61b7cc8a85a67...pdf
    855.8 KB · Views: 13
  • Vision-Combi-25-30C-User-Installation-and-Servicing-manual.pdf
    11.8 MB · Views: 13
Thanks for the helps guys.

UNG ... I did have a look and couldn’t see anything but I must have done something to cause the damage. Unless I have touched something or crossed something over and never realised. Either way, looks to be my fault I reckon.

The home owner got back to me saying BG came out, said I nearly caused a fire, all my connections were wrong (even though I disconnected all my connections and reinstated the original ones which was only LNE and the link) - which I doubled checked before I left and that I shouldn’t have been in the boiler connections as I’m probably not gas safe reregistered, to which the are reporting me for.

So things get worse.

I take responsibility for screwing the pcb, but I have never heard of having to be gas safety registered for connecting up a boiler. I always thought as long as you didn’t touch anything gas or air tight it was fine?

So I’m off boilers now. Any one recommend a training course or something? Will ask about my area see if any guys who mainly do them will let me tag a long for my own understanding.
 
Really sorry to hear about your boiler nightmare... but don't take it too seriously, just put it down to experience.

I'd largely ignore what BG say... they'll obviously try to 'big-up' themselves and belittle anyone else who may have created the problem they were there to fix.

I'm the same with boilers... I hate switching them off/on just in case it goes wrong. I have a specific clause about this in my Ts&Cs now.
 
Thanks for the helps guys.

UNG ... I did have a look and couldn’t see anything but I must have done something to cause the damage. Unless I have touched something or crossed something over and never realised. Either way, looks to be my fault I reckon.

The home owner got back to me saying BG came out, said I nearly caused a fire, all my connections were wrong (even though I disconnected all my connections and reinstated the original ones which was only LNE and the link) - which I doubled checked before I left and that I shouldn’t have been in the boiler connections as I’m probably not gas safe reregistered, to which the are reporting me for.

So things get worse.

I take responsibility for screwing the pcb, but I have never heard of having to be gas safety registered for connecting up a boiler. I always thought as long as you didn’t touch anything gas or air tight it was fine?

So I’m off boilers now. Any one recommend a training course or something? Will ask about my area see if any guys who mainly do them will let me tag a long for my own understanding.
Sounds like typical BG surprised the guy didn't try to sell the homeowner a rewire while he was there because the boiler wiring was dodgy
 
I am gas safe and electrical, FWIW, indeed the Hive 1,3 terms are supposed to be NV contacts, which you use to control the thermostat connections inside the boiler.
On the face of it i cannot see where this would not work.

The BG guy probably didn't like the cable from FSU to Hive and then to boiler, but thats just semantics.

Its also possible you were very unlucky, its not clear whether the PCB blew on call for DHW or whether than just coincided with a call for CH,

Either way you either wired it wrong, i.e. not as you have described or you were unlucky and the PCB blew because it had been powered down. It really does happen (alot)

BG guy can report if he wants but you are authorised to make those connections, so gas safe / HSE will probably ignore.

I understand why you may wish to avoid boilers, for me, if that happened i would have simply replaced the PCB, re-tested appliance and moved on.

It may be worthwhile, if you want to connect Hive's and the like, to know a gas safe buddy who you can call under these circumstances.

Hope this helps

P&S
 
I am gas safe and electrical, FWIW, indeed the Hive 1,3 terms are supposed to be NV contacts, which you use to control the thermostat connections inside the boiler.
On the face of it i cannot see where this would not work.

The BG guy probably didn't like the cable from FSU to Hive and then to boiler, but thats just semantics.

Its also possible you were very unlucky, its not clear whether the PCB blew on call for DHW or whether than just coincided with a call for CH,

Either way you either wired it wrong, i.e. not as you have described or you were unlucky and the PCB blew because it had been powered down. It really does happen (alot)
My thinking is exactly the same I cannot understand why it didn't work as it should

Assuming it was wired correctly the only thing I can think caused the problem was having the 240v and 24v in the same cable and a higher voltage was induced onto the 24v side than it could cope with

BG guy can report if he wants but you are authorised to make those connections, so gas safe / HSE will probably ignore.

I understand why you may wish to avoid boilers, for me, if that happened i would have simply replaced the PCB, re-tested appliance and moved on.

It may be worthwhile, if you want to connect Hive's and the like, to know a gas safe buddy who you can call under these circumstances.
Experience and having seen it before counts for a lot and I agree with you it happens occasionally and all you can do is learn from it and carry on
 
Thanks for the help guys.

I must have done something wrong and haven’t realised. It’s the only thing I can think of.

So I’m right in think then that as long as I’m not touching any gas / air tight, I am allowed in to the boiler to connect up?

I am going to do a bit of reading and see if there is any training courses or anything I can do for boilers.

Thanks guys.
 
Thanks for the help guys.

I must have done something wrong and haven’t realised. It’s the only thing I can think of.

So I’m right in think then that as long as I’m not touching any gas / air tight, I am allowed in to the boiler to connect up?

I am going to do a bit of reading and see if there is any training courses or anything I can do for boilers.

Thanks guys.
The MI's specifically state that the electrical connections must be carried out by a competent person to BS7671, thats you( i hope, lol)

Many boilers are engineered so that the external connections are accessible without too much dismantling. The only issue is that most modern boilers use the external case as a seal to enable it to be "Room Sealed", i.e. under no circumstances can nasty gases enter the room. The case is usually held on by one or two screws and clipped. As long as you replace the cover perfectly, its all good.

I only do commercial stuff and its why i have both electrical tickets and gas tickets, its to prevent a client being without heating under most circumstances. E.g Just before Xmas got called to no heating in a warehouse from Gas fired warm air heater. The problem was quickly diagnosed to be main air circulating fan motor. That was because of my electrical fault finding skills, as i also know a good motor supplier locally i managed to source a replacement and get the heater back working in less than 22 hours from initial call.

Another was an office combi boiler, no heat at all. Although diagnosis was largely an educated guess, i put my money and reputation on it being the pressure switch, although the manufacturer support line was less than impressive. I managed to source a replacement, next day and get it fitted.

So you can see why having good electrical skills is in-valuable when keeping modern stuff going.

The gas tickets are trickly to get, but in my view well worth the effort, and boilers are fun
 

Reply to Vokera Vision combi boiler in the Central Heating Systems area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock