Question:

What is actually going through the pipe? Is it power, or just an aerial coax? I see the attic hatch (aerial in the attic?), and i see the new socket (3 cables?) and you say that's near the corner of the room... so am i right in thinking the socket is going behind a telly?

I am thinking along the lines of, do the regulations apply when its not LV voltage running through the conduit?

reg 522.6.202 (prescribed zones) only mentions "a cable"
 
I am thinking along the lines of, do the regulations apply when its not LV voltage running through the conduit?

reg 522.6.202 (prescribed zones) only mentions "a cable"
I've not seen anything to exempt ELV cables - I imagine most houses are non-compliant in this respect. The common one will be a conduit run from the attic down to the living room for a TV aerial cable, with nothing in the bedroom above to indicate it's there.

There's always 522.5.204 (b) "be installed in earthed conduit complying with BS EN 61386-21 and satisfying the requirements of BS 7671 for a protective conductor"
Replace the plastic conduit with steel, earth it, and it's now compliant ;)
 
I suspect that chase is going to stay exactly where it is.
 