mstoker1990

Been to a right job today, alot of work needed to bring it up to spec.

A few questions im unsure with and its alot easier to ask on here than go through the regs.

The Use of RCD's is it a requirement on 16A Socket outlets in an area used for cutting meat?

are lights required to be RCD protected in an area where meat is cut? also these areas are pressure washed.

Also this place has two heating boilers.

Three supplies feed this lot, one feeds both boilers, one feeds the pump, one feeds the controls. Is this allowed or has it all got to pass through one isolator first? as if you turn the boiler isolator off potentially you still have live wires at the boiler from the controls feed, they are all fairly close together, but not right together.

Also two seperate supplies feed the same building, so how do you go about structural steel?


The poor fella thought everything was up to spec turns out to need alot of attention, if someone can help me out with those few questions it be great.

Cheers guys

Mark
 
In a commercial setting then there can be an exception for the RCD protection of socket outlets if they are not for general use by ordinary persons.
The lights will not need RCD protection, though they should be IP rated to at least IPX5 for the pressure washing.

If you have two supplies then you can label the points of isolation so that the second point of isolation is identified (more usual for main incoming dual supplies) but anyone working on the equipment in commercial environment should be testing for dead anyway and so will be safe.

Bonding of structural steel will be back to the main earth terminal for each supply. This will have the effect of joining the earthing systems but so long as they are the same it should not be a problem.
 
^^^^I agree but would add that if there are 3 seperate supplies to common heating components I would want 1 master isolation switch/fusing arrangement to turn the lot off together for safe working, what is the combined load for the heating arrangement?
 