no not haloween, i mean my day.
installing some 6 mm swa to outbuilding 24 mtrs,a sod of a job as around extension etc along walls.
anyways all cleated in glanded off one end and then i noticed that it wasn't 6mm more like 2.5 mm, it was quite dark at that time and i didn't want to check i just packed up my tools and said i would finish in the morning.
i have got the left overs in the van and after a beer or two will have a proper look.
my invoice says it's 6mm so either ive been riped off or my eysight is going will probably get back to you later.
 
garage will feed a tuble dryer a fridge and a light,from garage unit in outbuilding.
fed from ring in kitchen.
 
Been there my friend! Got 10mm instead of 16mm 4 core SWA, after slogging my nuts off 50 meters through a school loft later making my cable the only one neatly clipped! I came to gland and blamed the apprentice for not checking!
 
ok just checked its smaller than 6mm twin and earth and has 7 copper cores i am hopping its 4mm but am guessing its 2.5mm.
i wanted 3 core 6mm but they have given me 4 core, i was thinking if it is 2.5 can i double up on the cores and use swa as earth or would the swa be too small?
 
i mean the armouring as earth and the 4cores doubled to make 2 so theoretically i would have 5mm cable
 
it's tns by the way no rcd up front.

- - - Updated - - -

if i couldn't use armouring could i put a spike in?
 
Four core 2.5mm² SWA cable has a copper equivalent of 8.8mm² csa so it is suitable to use for a cpc for a 6mm² supply.
So long as you do not need to use it as a bonding conductor (but you would have been out of luck anyway with the 6mm) then you would be OK.
running the cables in parallel should be OK, will require some calculation to ensure it is suitable since 5mm² is not tabulated, but really as a first approximation good to go.
 
If it is 2.5mm 3 core single phase and clipped direct, you have 25A to play with. With the load your supplying it is ok.

If not, kick off with the wholesaler, demand the same length 2.5mm swa free f charge and extend the kitchen ring your tapping into lol. Imagine that, kitchen RFC extended to the garage with swa!!!! (dont think about doing it mate)
 
ok just checked its smaller than 6mm twin and earth and has 7 copper cores i am hopping its 4mm but am guessing its 2.5mm.
i wanted 3 core 6mm but they have given me 4 core, i was thinking if it is 2.5 can i double up on the cores and use swa as earth or would the swa be too small?

I can smell fish, herring the red variety.
Spill the bean's.
:confused5:
 
I had a 10mm 3 core delivered instead of a 32mm 4 core once.
I suggest you do the same as I did then and kick up hell with the supplier LOL
 
Hang fire!!! What size cleats did you use? Rather they were a loose fit or the wholesaler gave you the correct size cleats for the wrong size cable?????

Kaiser Chiefs said it best "I Predict a Riot".
 
Wholesalers can be very stupid when it comes to getting stuff right!! You do have to watch them, been stung a few times myself, now religiously check and double check everything before I install etc. Feel for you though buddy! Been there done that got the t shirt lol!
 