As well as that, the AM2 dropped the risk assessment for SPD which was introduced in the original 18th, again made practical sense as nobody will know the cable routing feeding a given site in many cases, but personally I would still advise folks to have SPD fitted if they have overhead lines feeding the site due to the greater risk of induced energy and the amount of valuable electronics folks have, even if they don't realise it (such as LED lights, most white goods having electronic controls and always-on, boilers with electronic controls, TV/PC/broadband, etc)
In such cases type 1 are a better choice as they can cope with more energy, but as you say they are not commonly stocked as the majority of installations do not have a Lightning Protection System, not do they have overhead lines feeding them. Yes, in the countryside they do, but that is small compared to the number in town and cities nearby.
Also type 1 are not cheap, both due to less demand and due to the
much bigger devices needed to cope (typically 10x the energy in the 10/350us pulse compared to the 8/20us pulse). We got some directly from here:
MAINS SPDs TO BS:EN 62305 Device selection information where External Lightning Protection is installed SPD PRODUCT SELECTOR Interactive...
kingsmillindustries.com
Early on they only had the double-module type 1+2 at vast expense, but they also now offer single-module ones and slightly less painful prices. An advantage of the double-width ones are the two terminals that makes Kelvin style connections easy and effective.
Even a type 2 SPD are better than nothing, but chances are they would fail after one high energy event and of course nobody ever monitors them, just as nobody ever checks their RCD (other then EICR time, and not even at that sometimes...)