I don't know the regulations in Indonesia where I guess you are based, but normally for us the design aspects are:
Maximum cable temperature rise and the degree of thermal insulation (open air, in duct, clipped to a wall, covered in insulation, etc) that gives the size needed to keep I^2R heating down to an acceptable level, so setting the current carrying capacity of the cable (ampicity in USA terminology).
Maximum voltage drop, so combination of cable length, acceptable drop (typically 5%) and cable impedance
Maximum earth fault loop impedance so the over-current protection device will disconnect fast enough (typically 5s for a sub-main and 0.4s for a final circuit) which needs the supply 'Ze' (earth fault loop impedance) as well as the type of OCPD and cable length.
For short cables you can usually concentrate on just the CCC, but you ought to evaluate all 3 aspects.