in the lounge there is one socket apparently installed recently which is one radial, it shares a B32 circuit breaker with a ring circuit, i thinking to make it code1 because B32 is wrong for a radial, but it looks not dangerous because the only one socket is only for a hoover sometimes, what do you guys think?

cheers
 
class it as an unfused spur. one socket outlet allowed. no code. but note it as a spur in comments. if you want to be picky, fit a FCU at the source of the spur.
 
in the lounge there is one socket apparently installed recently which is one radial, it shares a B32 circuit breaker with a ring circuit, i thinking to make it code1 because B32 is wrong for a radial, but it looks not dangerous because the only one socket is only for a hoover sometimes, what do you guys think?

cheers


Are you saying there are 3 x 2.5mm cables at the CU into one breaker/fuse?

If so I'd go for a "2"
 
if its only ONE socket outlet on the radial treat it as a Spur as this is allowed. If there are multiple socket outlets then this is wrong however as someone has already said I would personally fit a FCU for peace of mind
 
yes there are 3x2.5mm cables at the cu into one fuse, ok, got your point, code 2 agreed, cheers
 
Last edited by a moderator:
why code 2? an unfused spur with only 1 socket outlet is permitted.
 
Page 362 of 17th Edition, 2.5mm radial supplying a 2g socket is OK.

Doesn't make any difference whether the 3 cables are at the MCB or another socket backbox.
 
so the spur can be at the origin? theoretically it is, but not look nice really and bit confusing...
 
yes. it's perfectly OK. not the way i'd have done perhaps, but it complies to brb as yellowvanman said, so no problem. is there a spare way in the CU to fit a 16A MCB? this would satisfy God himself.
 