Lucien Nunes
Here's another organy one. This blower dates from 1936-7 and is still in use in its original installation. Slipring 18hp motor with 3-stage pneumatic rotor starter, drives dual-inlet main blower and 4-stage booster. Also drives 18.5V 100A generator to power the electric action, with separate 12V 30A exciter. The generator is interesting - it's rated for 100A continuous load but peak currents can be much higher e.g. when changing a lot of stops at once. The 18V circuits are heavy (19/.064) but some sections are long and drop can be 10-20%. So the generator is over-compounded, i.e. the series field has enough turns to increase the generated EMF by more than its internal drop as the load increases. The output terminal voltage rises one volt per 40A load, i.e. the dynamic resistance is -0.025Ω (yes that's negative resistance) which approximately cancels out the drop in the DC distribution cables and submains.