- Reaction score
- 1,289
Hi all, Scenario: A fused spur unit added to a ring main to supply several window actuators via an open / close rocker switch. The ring main is protected by a 32 Amp type B Mcb, the fused spur would only require a 5 amp BS 1362 fuse (lets say a 13 amp for worst case scenario in case replaced wrongly). The question is, when performing the Zs at the furthest window actuator, should the maximum ZS on the test sheet be 1.44 referring to the Ring Mcb or 2.42 referring to the 13 amp fuse (or even 3.83 as now for fixed equipment)? Many thanks in advance.