Hi im having to replace some old meter cable from the meter to the consumer unit , as it is around 6m in length i am going to fit a switch fuse unit , my question is what type of 25mm cable would you use and will it need a separate cpc other than the main 16mm main earth that is going to be run to the CU,also how would you wire it in , there is a double pole switch there at the moment so isolation shouldnt be a problem. Many thanks
 
Hey mate.

Is it a straight run to the C.U from the meter i.e up, down, sideways. Does it have to be concealed? can you use surface trunking? Also what size is the cut-out fuse??

If surface then 25mm tails with a 16mm earth in PVC trunking should be fine (depending on cut-out fuse). If you have to conceal then maybe an armoured or a concentric cable??

Spot on with the switchfuse if you can use tails then an MEM KMF would do if not, maybe a metalclad SF.

Cheers.
 
Hi lenny , the current cable is clipped up and along the cellar ceiling beam then up the side of the cellar steps to the top where the consumer unit is.The old cable is 10mm twin and what looks like 4mm main earth !

Cut out fuse says 100 amp but could be less , dont want to pull it
 
Last edited by a moderator:
Hey.

As it's down in the cellar then no need to conceal I'm guessing...
Is there any risk of damage with the route being close to the steps?? If not then I would say that 25mm tails and 16mm earth in a surface trunking - MT4 or 5 would be fine.

Cheers.
 
Cheers mate , if i use metalclad il probably run the 16mm earth into the sw fuse and out to the CU , ive got part p assesment coming up soon so got to get it right:eek:
 

Reply to what meter tail cable-cpc? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
387
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
709
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
On a new build site how/ why are people getting away with installing meter tails over 3metres in length and behind dot and dabbed walls with no...
Replies
7
Views
2K
Hi Guys Would I be correct in thinking an electric cable can be as close as 25mm to a gas meter ? (not that I'd ever be that close out of...
Replies
4
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock